Background
Several years ago I built a Kal-clone HERMS system following his design pretty closely. It has worked fairly well but I think I'm ready for the next step to streamline brewday even more. One of my frustrations is having to re-arrange tubes several times through the course of the brewday such as going from heating strike water, to filling mash tun, to filling the boil kettle, etc... I want to be able to automatically route water/wort where it needs to go with minimal interaction.
What this is: 240V 30A automated HERMS control panel wiring diagram and piping layout utilizing BruControl for all automation. The system uses 5500W heating elements in the HLT and Boil kettles, two 120V chugger pumps, automated ball valves to route water/wort/CIP water, proportional ball valves to regulate sparging rate and wort cooling rate, pressure sensors to monitor rough volume of water/wort in kettles, and RTD temperature sensors for control loop feedback and general temperature awareness.
Control Panel
Black wires and terminals are Line 1 AC, red wires and terminals are Line 2 AC, grey wires and terminals are Neutral, blue wires and terminals are 24V DC, orange wires and terminals are 5V DC, and purple wires and terminals are either 3.3V DC or analog voltage/current. Dashed lines are DC common; the color only references the corresponding DC voltage of the circuit it's used for. All DC commons should be connected together through the UniShield.
The thickest lines are 10 AWG, the middle thickness lines are 18 AWG, and the thinest lines are 22 AWG.
Two and three level terminals are used throughout. Black dotted arrow lines show terminals that are connected together with plug-in bridges.
All sensors interface through the BruControl MEGA Format UniShield, specifically an Adafruit Grand Central M4 Express. The UniShield allows me to save space by using slim-format din rail relays rather than the bulky Electronics Salon relays that are popular in designs. It also can be powered by 24V and creates a 5V output so I only need a single DC power supply (24V, 20A) for the entire system.
The DC section was originally going to be in its own panel. Since I'm still renting and have limited space, my thinking was it's easier to position, mount, and later move two smaller panels than it would be a single larger, heavier one. There would be connections for AC power from the AC panel and there would be Element Enable/Control and Pump Control signals going to the AC panel. The length of the components on each din rail (both AC and DC) is comparable (less than 13in) so there wouldn't need to be much if any panel layout changes to move all four din rails into a single panel.
My main goal when it came to panel layout and wiring is to minimize the amount of wires that have to cross and be routed around the box. My drawings attempt to show actual position of components on the din rail, albeit size of components not to scale. I tried to keep components that get wired together as close as possible on the din rail. For components that are connected between top and bottom din rails, I tried to vertically align/position them as close as possible.
I have an external GFCI breaker (from a SPA panel) that I plan to reuse. I've tried searching for din rail mounted GFCI breakers but have only been able to find ones that trip at 30mA (for machine safety) rather than the recommended 4-6mA (for human safety). Does anyone know of any din rail mounted GFCI breakers that trip at 4-6mA?
The element enable signals are connected through hardware interlock relays such that if somehow both elements get enabled at the same time, neither contactor will be energized. I've seen designs where a single "enable" relay is used and another signal connected to a DPDT relay controls whether it gets routed to HLT or Boil kettle. I chose my design instead because I didn't like the idea of having a bit in the software always be in either "HLT" mode or "Boil" mode.
I decided to connect the computer running BruControl to the Grand Central hardwired through a dedicated network switch. My wireless router is a floor above the brewery system and I've read a lot of posts complaining about getting wireless components connected and troubles with updating firmware over wifi. There will be an RJ-45 port on the side of the DC panel that I can plug my laptop into on brewday.
The DC side is powered off the black L1 breaker while the pump and heating element control AC are powered off the red L2 breaker. This will prevent a pump or heating element relay from tripping the breaker and killing the whole DC section.
The two terminals immediately to the right of the UniShield convert the 4-20mA current feedback signal from the proportional valves to a voltage signal for the Grand Central to read. The three terminals to the right of those are a simple voltage divider to bring the 5V signal of the Pressure Sensors to 3.3V.
Piping Diagram
On the piping diagram, valves with a circle are plain 2-way valves. Valves with a square are proportional valves. Valves with an "L" coming out of them are manual hand-controlled valves. Those are used for anything coming into the system or going out of the system. Green circles with a "T" are RTD temperature probes.
Although the piping diagram currently shows 13 2-way valves and 5 RTD probes, the DC drawing shows connections for 16 valves and 8 RTD probes. I wanted to reserve the space and connections in case the number of valves and RTD probes increased. I will likely trim down the number of relays, terminals, and external connections in the panel when I build it to save costs.
My biggest frustration on brewday is taking the kettles down and cleaning them by hand. When designing the piping, I wanted CIP capability to add water to the kettles, circulate with PBW, and flush out of the system. I've seen others use a Brew-In-A-Bag mesh bag in their Mash Tun for ease of removing grain and cleaning and I plan to do that as well. I took inspiration for the piping layout from several designs I've found online especially this post from the founder of BrewPi: https://www.homebrewtalk.com/forum/threads/automated-closed-system-herms-layout.490798/
The piping layout doesn't necessarily represent physical layout; it's laid out for ease of visualizing flow. I will probably have the water line near the bottom by the pumps instead of above the kettles. That will take a lot more thought and planning to simplify the physical piping paths.
----------------------------------------------
I haven't worked on anything BruControl related yet. I wanted to lock in the hardware design first to know exactly what I had to control before setting up the scripts.
I welcome any and all thoughts, comments, suggestions, criticisms, or ideas for improvements!
Several years ago I built a Kal-clone HERMS system following his design pretty closely. It has worked fairly well but I think I'm ready for the next step to streamline brewday even more. One of my frustrations is having to re-arrange tubes several times through the course of the brewday such as going from heating strike water, to filling mash tun, to filling the boil kettle, etc... I want to be able to automatically route water/wort where it needs to go with minimal interaction.
What this is: 240V 30A automated HERMS control panel wiring diagram and piping layout utilizing BruControl for all automation. The system uses 5500W heating elements in the HLT and Boil kettles, two 120V chugger pumps, automated ball valves to route water/wort/CIP water, proportional ball valves to regulate sparging rate and wort cooling rate, pressure sensors to monitor rough volume of water/wort in kettles, and RTD temperature sensors for control loop feedback and general temperature awareness.
Control Panel
Black wires and terminals are Line 1 AC, red wires and terminals are Line 2 AC, grey wires and terminals are Neutral, blue wires and terminals are 24V DC, orange wires and terminals are 5V DC, and purple wires and terminals are either 3.3V DC or analog voltage/current. Dashed lines are DC common; the color only references the corresponding DC voltage of the circuit it's used for. All DC commons should be connected together through the UniShield.
The thickest lines are 10 AWG, the middle thickness lines are 18 AWG, and the thinest lines are 22 AWG.
Two and three level terminals are used throughout. Black dotted arrow lines show terminals that are connected together with plug-in bridges.
All sensors interface through the BruControl MEGA Format UniShield, specifically an Adafruit Grand Central M4 Express. The UniShield allows me to save space by using slim-format din rail relays rather than the bulky Electronics Salon relays that are popular in designs. It also can be powered by 24V and creates a 5V output so I only need a single DC power supply (24V, 20A) for the entire system.
The DC section was originally going to be in its own panel. Since I'm still renting and have limited space, my thinking was it's easier to position, mount, and later move two smaller panels than it would be a single larger, heavier one. There would be connections for AC power from the AC panel and there would be Element Enable/Control and Pump Control signals going to the AC panel. The length of the components on each din rail (both AC and DC) is comparable (less than 13in) so there wouldn't need to be much if any panel layout changes to move all four din rails into a single panel.
My main goal when it came to panel layout and wiring is to minimize the amount of wires that have to cross and be routed around the box. My drawings attempt to show actual position of components on the din rail, albeit size of components not to scale. I tried to keep components that get wired together as close as possible on the din rail. For components that are connected between top and bottom din rails, I tried to vertically align/position them as close as possible.
I have an external GFCI breaker (from a SPA panel) that I plan to reuse. I've tried searching for din rail mounted GFCI breakers but have only been able to find ones that trip at 30mA (for machine safety) rather than the recommended 4-6mA (for human safety). Does anyone know of any din rail mounted GFCI breakers that trip at 4-6mA?
The element enable signals are connected through hardware interlock relays such that if somehow both elements get enabled at the same time, neither contactor will be energized. I've seen designs where a single "enable" relay is used and another signal connected to a DPDT relay controls whether it gets routed to HLT or Boil kettle. I chose my design instead because I didn't like the idea of having a bit in the software always be in either "HLT" mode or "Boil" mode.
I decided to connect the computer running BruControl to the Grand Central hardwired through a dedicated network switch. My wireless router is a floor above the brewery system and I've read a lot of posts complaining about getting wireless components connected and troubles with updating firmware over wifi. There will be an RJ-45 port on the side of the DC panel that I can plug my laptop into on brewday.
The DC side is powered off the black L1 breaker while the pump and heating element control AC are powered off the red L2 breaker. This will prevent a pump or heating element relay from tripping the breaker and killing the whole DC section.
The two terminals immediately to the right of the UniShield convert the 4-20mA current feedback signal from the proportional valves to a voltage signal for the Grand Central to read. The three terminals to the right of those are a simple voltage divider to bring the 5V signal of the Pressure Sensors to 3.3V.
Piping Diagram
On the piping diagram, valves with a circle are plain 2-way valves. Valves with a square are proportional valves. Valves with an "L" coming out of them are manual hand-controlled valves. Those are used for anything coming into the system or going out of the system. Green circles with a "T" are RTD temperature probes.
Although the piping diagram currently shows 13 2-way valves and 5 RTD probes, the DC drawing shows connections for 16 valves and 8 RTD probes. I wanted to reserve the space and connections in case the number of valves and RTD probes increased. I will likely trim down the number of relays, terminals, and external connections in the panel when I build it to save costs.
My biggest frustration on brewday is taking the kettles down and cleaning them by hand. When designing the piping, I wanted CIP capability to add water to the kettles, circulate with PBW, and flush out of the system. I've seen others use a Brew-In-A-Bag mesh bag in their Mash Tun for ease of removing grain and cleaning and I plan to do that as well. I took inspiration for the piping layout from several designs I've found online especially this post from the founder of BrewPi: https://www.homebrewtalk.com/forum/threads/automated-closed-system-herms-layout.490798/
The piping layout doesn't necessarily represent physical layout; it's laid out for ease of visualizing flow. I will probably have the water line near the bottom by the pumps instead of above the kettles. That will take a lot more thought and planning to simplify the physical piping paths.
----------------------------------------------
I haven't worked on anything BruControl related yet. I wanted to lock in the hardware design first to know exactly what I had to control before setting up the scripts.
I welcome any and all thoughts, comments, suggestions, criticisms, or ideas for improvements!