Depending on the size of your over current protection device it will take anywhere from 15 to 50 amperes for quite a few cycles to clear a fault and it only takes 50milliamperes to kill you, a GFCI designed to protect persons will clear at an imbalance of ~5mA for ~2cycles.
A circuit breaker is designed to protect property, a GFCI is designed to protect life.
Also there is a potential for a GFCI to catch a fault before it becomes a dead short or ground fault.....just because a breaker says it clears at 15A does not mean that is the maximum current it will see because it takes several cycles to clear. This is the reason most branch circuit breakers are rated at 10000 amperes RMS symmetrical and mains are rated much higher ~21K amperes RMS symmetrical. A typical home may see current in the excess of 9KA during an event. I work in industry so the risk is much higher, this is why Arc flash is pushed so heavily in our trade.